TN-C-S系统中的TN,C,S分别的英文单词是什么?不要中文,谢谢!
' f2 Q3 e; D( L. j  a' h# n3 Y+ t) K4 Q/ m' n. J  w5 D
[ 本帖最后由 bdblbyq 于 2007-7-11 12:34 编辑 ]
发表于 2007-7-10 18:05:52 | 显示全部楼层 来自: 中国河南南阳

仅供参考

Terra Neutral-Combined-Separate
& \5 V! C+ A! d( m& b0 L& y+ m% a; _! \/ \! Y& I5 S
6 a  n' l* Q: h* C0 o1 T# I$ _) _
/ ~0 O( m8 x, T+ ~, {
International standard IEC 60364 distinguishes three families of earthing arrangements, using the two-letter codes TN, TT, and IT.# ^5 S# q2 N9 I5 [6 k' E5 V
8 b* p3 z4 U/ t6 X2 i& H6 F7 m
The first letter indicates the connection between earth and the power-supply equipment (generator or transformer):
+ W$ W% Y1 L) l5 j6 }4 \
6 X/ g& i% @1 PT  :  direct connection of a point with earth (French: terre); . c+ J1 C4 l, L5 w9 _
I  :  no point is connected with earth (isolation), except perhaps via a high impedance.
& F  |9 K/ P* ^" v6 `
! O; ]& V8 T0 M6 [: X0 zThe second letter indicates the connection between earth and the electrical device being supplied:
6 q- Q9 G! w; ?5 {1 j: L' ?- {4 i2 T' t' k/ T
T  :  direct connection with earth, independent of any other earth connection in the supply system; & Z  l6 k: C- T: _& ]! W: Y5 V' t
N  :  connection to earth via the supply network 2 o% e& \9 |7 r! v
8 h- Q9 [: |0 G$ S

1 {" n8 w, I. P# yThe conductor that connects the exposed metallic parts of the consumer is called protective earth (PE). The conductor that connects to the star point in a three-phase system, or that carries the return current in a single-phase system, is called neutral (N). Three variants of TN systems are distinguished:; K! q( n$ O. Q0 W! H" f! T( {
( a  y1 w, x( s7 i* `& q, e, `
TN‑S  :  PE and N are separate conductors that are connected together only near the power source.   P4 N# V* p5 X
TN‑C  :  A combined PEN conductor fulfils the functions of both a PE and an N conductor.
) [" E& ?  N$ j7 G+ |; t& P$ dTN‑C‑S  :  Part of the system uses a combined PEN conductor, which is at some point split up into separate PE and N lines. The combined PEN conductor typically occurs between the substation and the entry point into the building, whereas within the building separate PE and N conductors are used. In the UK, this system is also known as protective multiple earthing (PME), because of the practice of connecting the combined neutral-and-earth conductor to real earth at many locations, to reduce the risk of broken neutrals - with a similar system in Australia being designated as multiple earthed neutral (MEN).

评分

参与人数 1三维币 +5 收起 理由
bdblbyq + 5 应助

查看全部评分

 楼主| 发表于 2007-7-11 09:21:30 | 显示全部楼层 来自: 中国北京

很详细

很详细,谢谢!有关它的英文标准吗?