[已解决] TN-C-S系统中的TN,C,S分别的英文单词是什么?

 关闭 [复制链接]
发表于 2007-7-10 09:16:17 | 显示全部楼层 |阅读模式 来自: 中国北京

马上注册,结识高手,享用更多资源,轻松玩转三维网社区。

您需要 登录 才可以下载或查看,没有帐号?注册

x
TN-C-S系统中的TN,C,S分别的英文单词是什么?不要中文,谢谢!. ~8 S- ~; Q4 I2 G
- m* K/ t1 T2 p4 Q' \" J
[ 本帖最后由 bdblbyq 于 2007-7-11 12:34 编辑 ]
发表于 2007-7-10 18:05:52 | 显示全部楼层 来自: 中国河南南阳

仅供参考

Terra Neutral-Combined-Separate
* z3 r& V9 ?, Q! f1 v- D0 n
/ X* @! K2 D" ^3 H& O4 X, ?" l( L, H
! {7 e- K: h, t3 ?! u9 @3 V" j9 z4 V
International standard IEC 60364 distinguishes three families of earthing arrangements, using the two-letter codes TN, TT, and IT., _$ X1 O: j: ^
9 P- ^6 g) x, u& a. H6 |
The first letter indicates the connection between earth and the power-supply equipment (generator or transformer):2 S8 N' T! J/ F

- L6 o/ x% J6 `: sT  :  direct connection of a point with earth (French: terre); , C/ p4 u& c- @/ o6 r( B1 o. ~+ _
I  :  no point is connected with earth (isolation), except perhaps via a high impedance.
1 o0 u% {! _8 Y3 B0 m2 G9 c; [/ L2 v' T! v" B
The second letter indicates the connection between earth and the electrical device being supplied:- M) Z5 T* o# Q; B" e! @, m

, p( i4 @9 Y! d! ~9 q2 H! WT  :  direct connection with earth, independent of any other earth connection in the supply system; 4 L, S1 `  [6 t
N  :  connection to earth via the supply network
. l& H, A8 c6 F; e( [' X0 d8 l) S, \4 U& j* P- i
! S% R6 M! V1 B5 ]! I6 j- S
The conductor that connects the exposed metallic parts of the consumer is called protective earth (PE). The conductor that connects to the star point in a three-phase system, or that carries the return current in a single-phase system, is called neutral (N). Three variants of TN systems are distinguished:
) A0 z! p5 u; b' E- f/ q* _$ E0 Y- L% g8 t6 G
TN‑S  :  PE and N are separate conductors that are connected together only near the power source.
3 ~$ s, t- W  ]TN‑C  :  A combined PEN conductor fulfils the functions of both a PE and an N conductor. 4 E* w- t* A7 g' n
TN‑C‑S  :  Part of the system uses a combined PEN conductor, which is at some point split up into separate PE and N lines. The combined PEN conductor typically occurs between the substation and the entry point into the building, whereas within the building separate PE and N conductors are used. In the UK, this system is also known as protective multiple earthing (PME), because of the practice of connecting the combined neutral-and-earth conductor to real earth at many locations, to reduce the risk of broken neutrals - with a similar system in Australia being designated as multiple earthed neutral (MEN).